I can not increase the setpoint high limit of 2408 controller higher than 850 C.

We are using a Eurotherm 2408 PID controllers in one of DC power supply. I try to increse the setpoint high value to 1000 C however I cannot go above 850 C. I have checked the manual but I was not able to find a solution. COuld you please advise a solution such that I can increase max temperature to 1000 C.
1 person has
this question
+1
Reply
  • Bob Anderson (Technical Support Engineer) August 20, 2014 09:30
    Hello Suleyman,

    Providing you are using a thermocouple range capable of increase to this value please use the following method.

    Enter Full level.

    Page to SP List.
    Scroll to SP H.
    Increase the Setpoint high limit from 850.

    If this does not work.
    Enter Config Level.
    Page to PU.
    Scroll to rnG.H
    Increase the value to 1000 or beyond.

    Exit from Config and adjust the SP High limit described above.

    If all fails please indicate what sensor you are using.